Grounds and Neutral
Alwayslearningelec
NJ
Estimator
Where can I read and learn about when circuits require neutrals and grounds. I know that you can use conduits as a ground sometimes but I also know there are many different scenarios for the use of grounds and neutrals. Thanks.
Article 200 "Use and Identification of Grounded Conductors"
Article 250 "Grounding and Boding"
Grounding = Ground
Grounded = Neutral
Think of the above two words in their verb form: Grounding implies that the action is continuous and incessant. Grounded implies that the act of grounding has happened. While this may be a bit fuzzy, think of it as you read through the two articles mentioned.
Circuits almost always need grounds and neutrals are required where there is equipment that need them. Of course, a neutral must be brought to the service disconnect but need not go any further if there is no call for one.
There are numerous places in the code where conduit is not accepted as a egc but generally metallic conduit is acceptable. Pools are one area where an insulated ground is required. Isolated ground recep. where req. must also have an insulated ground.
I guess there isn't one book that will tell you all this info other than the Nec
Thanks......
I have never read Mikes book, I am sure it is great. If you are looking for something else:
Soares Book on Grounding and Bonding
Edit: Nevermind already posted Durrrrrrrr.