luckyshadow
- Maryland
Ok-
A few of us are debating Article 605.6.
Basically 605.6 says that multiwire branch circuits feeding partitions shall be provided with a means to simultaneously disconnecting all ungrounded conductors at the panelboard.
Now most systems furniture comes wired with 4 circuits, and the whip has 4 hot conductors and 2 neutral conductors.
Some folks are arguing that the electrician must use a 4 pole breaker or provide handle ties to disconnect all 4 circuits based on 605.6
I say that the electrician can use a 3 pole breaker ( or approved handle ties) and a single pole breaker.
I base this on article 100, the definition of a multiwire circuit is :
Branch circuit,Multiwire:
A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system
I based my opinion on the part of the definition that says " two or more ungrounded conductors that have a voltage between them"
A 4wire "circuit" will not have voltage between ALL 4 ungrounded conductors.
Thoughts and opinions welcomed !