I received the following email and am passing it along for comments:
We have a somewhat unique situation in that an isolation transformer mfg is proposing to add a 120:120V isolation transformer within a pad-mount utility transformer as a solution to re-feed existing street lights that are presently fed by 120 volt, 2 wire circuits without a ground > conductor brought to each metal street light circuit.
The isolation transformer mfg has indicated it will make a safer installation as a
solution to solve the existing situation of: an existing metal pole was energized at 90-100 volts (measured from metal pole to earth) as an internal fault to the pole occurred and did not clear an upstream over-current protective device and the pole remained energized.
As a temporary solution, the utility installed a ground rod and bonded the rod to the light pole to no avail, which resulted in the same measured touch potential (90-100V) as before and the measured current increased from 4 amps to 10 amps, since no ground conductor existed to create a low-impedance path back to the source to trip an OCPD. To come up with a low cost solution, the utility found an isolation transformer manufacturer that has applied their iso xfmr out east as a solution in > lieu of adding a ground conductor. (approximate cost = $1M to add ground conductor)
We have a somewhat unique situation in that an isolation transformer mfg is proposing to add a 120:120V isolation transformer within a pad-mount utility transformer as a solution to re-feed existing street lights that are presently fed by 120 volt, 2 wire circuits without a ground > conductor brought to each metal street light circuit.
The isolation transformer mfg has indicated it will make a safer installation as a
solution to solve the existing situation of: an existing metal pole was energized at 90-100 volts (measured from metal pole to earth) as an internal fault to the pole occurred and did not clear an upstream over-current protective device and the pole remained energized.
As a temporary solution, the utility installed a ground rod and bonded the rod to the light pole to no avail, which resulted in the same measured touch potential (90-100V) as before and the measured current increased from 4 amps to 10 amps, since no ground conductor existed to create a low-impedance path back to the source to trip an OCPD. To come up with a low cost solution, the utility found an isolation transformer manufacturer that has applied their iso xfmr out east as a solution in > lieu of adding a ground conductor. (approximate cost = $1M to add ground conductor)