To sleeve or not to sleeve

Status
Not open for further replies.

mark32

Senior Member
Location
Currently in NJ
In conjunction with my other post (Drilling through brick..) how many of you sleeve romex or low voltage cable when passing through concrete and/or brick?
 

mark32

Senior Member
Location
Currently in NJ
Thanks for the replies. I'm not too concerned for ease of passing the cable(s) through, it's the ease of drilling that interests me more. I think we determined a while back that romex should be sleeved but I just wondered how many actually do it.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
(A) Type NM. Type NM cable shall be permitted as follows:
(1) For both exposed and concealed work in normally dry
locations except as prohibited in 334.10(3)
(2) To be installed or fished in air voids in masonry block
or tile walls
I think the hole you drilled counts as an air void.
 