Residential Bathroom Lighting
Eagle126
We are gutting and wiring a residential bathroom, There is an existing 15 amp non gfci circuit for bathroom lighting, and shower lighting, does this circuit need to be gfci protected? Is a 15 amp circuit ok for this application. There will also be a 20 amp circuit for the outlet inside this bathroom.Thanks Mike P
Sounds ok to me. You should check out 410.10(D)
Article 210.8 will tell you where GFCI is needed. Unless specific equipment requires GFCI then you will follow 210.8.
15 amp circuit is fine for lighting.
Some fans and or lighting may need GFCI protection if installed in the shower areas.