EGC vs. GEC
sparky723
Haskell,Tx
Whats the difference?
I think an egc is the wire from neutral to cabinet or enclosure
and gec is the wire from panel to ground rod or tranx to water pipe.
Why do I keep getting these mixed up?
Is there a 3rd grade way to remember them apart for the test?
charlie b
Lockport, IL
Retired Electrical Engineer
Yes there is. Spell out the words. It helps slightly that the "C" word is the same in both cases.
  • GEC - Grounding Electrode Conductor. The phrase "grounding electrode" is the ground rod (or other thing that is stuck into the dirt). So the GEC is the wire that goes from the service point to the dirt.
  • EGC - Equipment Grounding Conductor. This has to do with equipment. This is the green wire you attach to the external metal parts of equipment, and the one that provides a path for fault current to flow back to the source. I have heard it called the "safety ground."