Closet fluorescent
Maine
Does anyone know the manufacturer/model of a surface mount flrscnt that is identified for use in a closet storage space.
Thanks
Sorry, posted this under the wrong topic and don't know how to change it.
Leviton makes one, I have seen it on the wall rack at my wholesale house, its a CFL type. If I stop by today I will get you the part number.
The only fixture that is required to be suitable for closets is an LED. Any fluorescent will work if it meets the distances.
I know that's what it says in the commentary of the NECH but it that what the requirement really says?
Not exactly you are correct. This is for LED lights that are installed within the storage area. Other lights are not allowed in the storage but LED surface style are as well as fluorescent if they are suitable.
Here is the article.
410.16(C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
(1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
(2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
(3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
(4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
(5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use.
I don't think either of the Leviton fixtures mentioned above are "identified for use WITHIN the closet storage space."
From Leviton
"Installs in closets, garages, basements, utility rooms and attics"
I'm assuming the OP is looking for a fixture that meets the requirements of 410.16(C)(5) that could be installed anywhere in a closet, including directly above a storage shelf. (ie. "within the storage space") These handy Leviton fixtures need to be mounted 6" away from the storage space like any other florescent fixture.
We always use fluorescent undercabinet lights with lens mounted on wall directly above the door. Most new installs get door jamb switch but occ sensors work also. No need to worry about light being left on when door is closed.