Does anyone know the manufacturer/model of a surface mount flrscnt that is identified for use in a closet storage space.

Thanks

Sorry, posted this under the wrong topic and don't know how to change it.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The only fixture that is required to be suitable for closets is an LED. Any fluorescent will work if it meets the distances.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I know that's what it says in the commentary of the NECH but it that what the requirement really says?
Not exactly you are correct. This is for LED lights that are installed within the storage area. Other lights are not allowed in the storage but LED surface style are as well as fluorescent if they are suitable.
Here is the article.

410.16(C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
(1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
(2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
(3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
(4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
(5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use.
 

gary

Senior Member
Location
California
Occupation
Retired electrical contractor / general contractor
I don't think either of the Leviton fixtures mentioned above are "identified for use WITHIN the closet storage space."
 

gary

Senior Member
Location
California
Occupation
Retired electrical contractor / general contractor
From Leviton
"Installs in closets, garages, basements, utility rooms and attics"

I'm assuming the OP is looking for a fixture that meets the requirements of 410.16(C)(5) that could be installed anywhere in a closet, including directly above a storage shelf. (ie. "within the storage space") These handy Leviton fixtures need to be mounted 6" away from the storage space like any other florescent fixture.
 

rbwsparky

Senior Member
Location
Sewickley,PA
We always use fluorescent undercabinet lights with lens mounted on wall directly above the door. Most new installs get door jamb switch but occ sensors work also. No need to worry about light being left on when door is closed.
 