stjohnbarleycorn
I have a peninsula that is 6 foot long, and 24" wide, with not cooktop or sink or any break in the top. I am required to put one outlet on the peninsula. As far as I can see it can be anywhere. I also need one on the wall that the peninsula is connected too. Although not practical can you put it right next to the wall, on the peninsula, the customer does not want to put any in, and close to the wall end would be their next best idea. thanks.
1) Wall Countertop Spaces. A receptacle outlet shall be installed at each wall countertop space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space.
(3) Peninsular Countertop Spaces. At least one receptacle outlet shall be installed at each peninsular countertop space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. A peninsular countertop is measured from the connecting edge.