Wye-Wye
Mike01
MidWest
Wye-Wye? Why would you use this type of transformer? I have just seen a drawing that had a substation with a primary switch and the transformer (1500/1995Kva) at 12470-480Y/277V. The drawings and specifications called for the transformer to be a ?5-leged core? for a Wye-Wye. My question is why not connect the transformer as a delta-wye is there any advantage to a wye-wye? This type will also allow currents to flow to the primary also correct?
Is that a philosophical question? ;)
First of all, just about every modern wye service these days is wye-wye.
The only advantage I can think of is independent operation, meaning minimal load loss with the loss of a primary conductor.
There are others here much more familiar with utility systems than I am.
That's really beyond my expertise, but I believe so. A wye-wye literally is three 1ph transformers that merely share a conductor.
I'm thinking that if a primary is truly connected wye and one leg is lost, either the winding or its feed conductor, service is maintained on the other two legs to neutral. If the primary were connected delta and one leg was lost, all three secondary phases would be affected.
OK, I understand that.
If one leg of the primary was lost it would affect two primary windings since each phase feeds two windings, why would the 3rd winding be affected? I don't get it.
While it blocks most of the 3rd harmonics, the Delta-Wye has an issue with a loss of a primary phase in that you can get very high voltages which also cause high current unbalances; motors hate it when that happens.
3rd Harmonics will flow.
... the Delta-Wye has an issue with a loss of a primary phase
Mivey,
That is an interesting idea.
Could you elaborate, just one step further,
and help me visualize this concept. :)
OK, I understand that. If one leg of the primary was lost it would affect two primary windings since each phase feeds two windings, why would the 3rd winding be affected? I don't get it.
Each line powers all three windings in a delta-fed, wye-configured primary. Take away one leg of power and there is nothing to pull the floating neutral to the 120? phase angle relationship for the other two windings. The two energized windings would be series-connected line-to-line. If the primary neutral were connected, the windings would still be line-to-neutral on the loss of one leg.
OK, thanks. I misunderstood your other post. I thought you were saying a delta connected primary (on the transformer) but you were talking about a delta primary connected to the transformer in a wye configuration on the transformer primary with the neutral floating. Right?
Right (if I understood you correctly ;)). :)
I generally refer to the feeder connection as "connected", and the winding-to-winding arrangement as "configured".