I am in a strip mall unit. Service was recentlly updated (by others) form (1) 200 amp panel to (2) 200 amp panels fed by a 400 amp disc. 150 feeet away at the end of the building. The water main is directly below the panels and has no bond, and a gas line in the attic with no bond. There is a ground rod below the disc. and it is attached to the neutral bar by a #6. The EGC ran to the panel is attached to a ground bar in the disc. seperate from the neutral bar. Now for the questions. Please correct me if I am wrong. Shouldn't the ground bar in the disconnect be attached to the neutral bar by a MBJ. Shouldn't the water main and gas line be attached directly to the neutral bar by a seperate GEC ran direclty and unbroken to the water bond and the gas line. Or... Can the water and gas be attached at each ground point in the panels.