I have an Analyzer Bldg that I'm not completely sure is classified correctly. I'm new to area classification and would like a second opinion.
Background Info: The bldg is 8ft wide x 8ft deep x 8ft tall with forced ventilation (standard window unit). It is not pressurized as per NFPA 496. The bldg has two Hydrogen Cylinders (used as a carrier gas) located on the exterior of the building. A flow restrictor in the line where the H2 is entering the building will limit the H2 to approx. 15 L/Hr on the interior of the bldg. Also, the bldg has 2 LEL detectors that continually monitor the LEL level inside the bldg.
Per the building manufactuer, the interior and exterior rating of the building is Class 1 Div. 2 Group C&D. I thought that when Hydrogen was present it becomes a Group B area. The manufactuer states that the 15 L/Hr restrictor and forced ventilation is sufficient to dilute the level of H2 inside the shelter in case there is any leak of H2.
Is there an NFPA standard or some other document that discusses the volume of H2 required to make an area Group B? I did not see it in NFPA 497 (or maybe I'm not interpreting the tables correctly). The two exceptions in the NEC for Group B are for gases other than Hydrogen. If someone could point me in the right direction I would greatly appreciate the help. Thanks,