A anbm Senior Member Location TX Occupation Designer Aug 16, 2010 #1 Is the clearance required for ground bar inside electrical room rather than the ground bar needs to be accessible?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Aug 16, 2010 #2 What do you mean by clearance, are you really referring to accessibility?
A anbm Senior Member Location TX Occupation Designer Aug 17, 2010 #3 3' clearance at front, no obstacles.
charlie b Moderator Staff member Location Lockport, IL Occupation Retired Electrical Engineer Aug 17, 2010 #4 The ground bar is not included in the list of electrical equipment that is likely to be worked on while energized. It is never energized. So there are no requirements for working clearance in front of the ground bar.
chris kennedy Senior Member Location Miami Fla. Occupation Retired electrician Aug 17, 2010 #5 charlie b said: It is never energized. Click to expand... Under normal operating conditions. All bets are off if there is an open grounded conductor at the service.