Senior Member
Installing a recptical on the outside wall of a batheroom. It is with in 6 feet of the sinck but the bathroom has a door on it. Must it be a gfci. What code ???
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I think a bathroom sink could still be considered a "utility sink", so if a 6' cord can reach the edge of the sink from a receptacle, GFCI would still be required per 210.8 (7).

Steve
 

wireguy8169

Senior Member
Location
Southern Maine
Other than dwelling unit

Other than dwelling unit

210.8 (B) (5) deals with other than dwelling unit that requires the GFI with in 6' of a sink. And as was stated before if its not in the same area its not part of that area.(other than maybe a few exceptions) And so should not be required
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Installing a recptical on the outside wall of a batheroom. It is with in 6 feet of the sinck but the bathroom has a door on it. Must it be a gfci. What code ???
If you get red tagged for that then I will gladly come and help you put the insp. out of his/her misery. :grin:
 