max overcurrent protection size?
J-R
New Jersey
What would be max size overcurrent protection for this situation?
24 #10 thhn in 1 1/2 emt (ambient temp 100f) branch circuits serving continuous lighting load and multi outlet recepticles?
#10 thhn 40a
ambient temp adj .91
310 15 b2a correction 45%
40x.91x.45=16.38
240.4 b1 is not met because of mulit outlet recepticles branch circuit
does 1.25% for continuous load apply in this situation?
I would think 15a would be max
Thanks for any help
So we have no idea what the load is. If the load is 10 amps then a 20 amp breaker could work. This is a bad question. The 125% does not enter into the equation, IMO.
IMHO, 15 amp would be the max OCP for the conductors feeding any multi-outlet branch circuits feeding cord and plug connected portable laods.
Your continuous lighting would have to be calculated at 125% so with a conductor ampacity of 16.38, the lighting load would be limited to 13.1 amps but could be on a 20 amp OCP device.
What im trying to understand is as long as your calculated load is under 16.3a
it would still be ok to use a 20A breaker in this situation?
Add these...
The distance (might be required to be considered) and including a deduction count of the sum of the fill of the conduit itself!
Your item circuit load is individual and a sum of individual loads to the circuits served needs to be determined and established!
Hope that helps...