In order to determine existing load in an existing building that we do some rennovation, assume we do not have demand data electrical consumption load for one year, we can use the exception for 30 days metering record - and use that metering data for our calculation. Does anyone actual run into any inspectors that actual want to see 30 days metering result, sometimes 30 days metering task will costly and kill the project budget. Thanks!
220.87 Determining Existing Loads. The calculation of a feeder or service load for existing installations shall be permitted to use actual maximum demand to determine the existing load under all of the following conditions:
(1) The maximum demand data is available for a 1-year period.
Exception: If the maximum demand data for a 1-year period is not available, the calculated load shall be permitted to be based on the maximum demand (measure of average power demand over a 15-minute period) continuously recorded over a minimum 30-day period using a recording ammeter or power meter connected to the highest loaded phase of the feeder or service, based on the initial loading at the start of the recording. The recording shall reflect the maximum demand of the feeder or service by being taken when the building or space is occupied and shall include by measurement or calculation the larger of the heating or cooling equipment load, and other loads that may be periodic in nature due to seasonal or similar conditions.
(2) The maximum demand at 125 percent plus the new load does not exceed the ampacity of the feeder or rating of the service.
(3) The feeder has over-current protection in accordance with 240.4, and the service has overload protection in accordance with 230.90.