I have roughed in 1 and 2 gang masonry boxes in a block wall. On the open face of box side is a class 2, division 2 rated area. Are my boxes considered in the area? Do they have to be changed? (impossible now) or are surface mount devices suitable? I've searched the NEC, and cannot get a direct answer for my question. Can anyone help me with this?
 
I have roughed in 1 and 2 gang masonry boxes in a block wall. On the open face of box side is a class 2, division 2 rated area. Are my boxes considered in the area? Do they have to be changed? (impossible now) or are surface mount devices suitable? I've searched the NEC, and cannot get a direct answer for my question. Can anyone help me with this?


I would say they are not allowed if they are in the CL II Div II area.
502.10 (B) (4) 2008 NEC
 
would the inside of a block wall- encased in cement be considered dust-tight?


Are the block walls filled with concrete, and if not is the box within the wall subject to the class 2 environment?

Whatever covers the flush box opening needs to be dust tight.
 