FRANK ELECTRIC
- PA
The job I am specifing is: the customer wanted Her existing 100 amp panel replaced, it was currently in the bathroom so after assessing the job I determined that relocating the panel on the same wall just in another room was going to be the most cost efficient way to accomplish this. As You can see in the pictures, I used a 2" pipe to connect the old panel to the new panel for the branch conductors, My question is this: what code section(s) require Me to route each individual grounded conductor (neutral) from the existing panel to the new panel? Would it be acceptable to route one, two or however many larger conductors for the branch neutrals (in the new panel)that would equal or exceed the circular mills of the combined individual neutral's in the old panel? To be safe I did route each neutral individually although I'm just curious. The old panel is an accessable junction box (by removing screws) where I spliced the branch wiring.
Note: I would have replaced / relocated the meter (reccomended it to the customer) due to round type and unaccessable since a room was built around it) although she didn't have the funds at this time. The Splices for the service enterance are crimp (irreversable) type connections also.