I am trying to learn as much as possible for a project I will be working on soon to ground my first substation.
I am reading through IEEE 142 to get my feet wet. and came to section 2.7.4.4 which gives an example of calculating the thermal energy (I2t) based on available informtion.
I followed the equation given in a previous section and it made perfect sense, but now in the application.... I must be doing something really wrong.
Here's the given information:
400 A feeder with a No. 3 AWG equipment-grounding conductor sized from the reference Table 250-95. Using an initial temperature of 60 deg C and a final temperature of 250 deg C for cross-linked polyethylene insulation, I2t = 17.8 x 10^6.
And here's the applicable equation:
I2t = A*[0.0297 log ((Tm + 234) / (Ti + 234))]
Where:
t = time of fault-seconds
I= fault current through conductor-amperes
A= conductor cross-sectional area-circular mils
Ti= initial operating temperature- degrees Celsius
Tm = maximum temperature for no damage - degrees Celsius
From tables I find A = 52620 cmils
and solving I2t = 338.35
This is only off by about 3 orders of magnitude. So, I'm certain I'm doing this wrong, but I don't see where.
Can anyone clarify this mess for me?
Where: