G gtlegget Member Location Plainfield NJ Aug 25, 2010 #1 Please settle a disagreement, I won't say who is on what side. Is the above titled (Type SOW SOW-A) listed and aproved for use in rigid conduit, Thanx in advance>
Please settle a disagreement, I won't say who is on what side. Is the above titled (Type SOW SOW-A) listed and aproved for use in rigid conduit, Thanx in advance>
raider1 Senior Member Staff member Location Logan, Utah Aug 25, 2010 #2 Take a look at 400.8(6) and 400.14. As a general rule flexible cord is not permitted to be installed in a raceway. In industrial establishments there are some exceptions. Chris
Take a look at 400.8(6) and 400.14. As a general rule flexible cord is not permitted to be installed in a raceway. In industrial establishments there are some exceptions. Chris
G gtlegget Member Location Plainfield NJ Aug 25, 2010 #3 Submesible pump set Clas 1 div 2 environment, explosion proof starter, E-Y w chico seal