grounding
anthony81
service ground in single family residence came from water main and was landed on neutral bar. correct problem by installing ground bar into panel..
Welcome to the Forum. :)
Do you have a question? You first sentence does not contain a problem.
I agree with Rob about your first sentence.
After your modification, are you saying the neutral is not bonded to the GEC?
Roger
The gec from the water pipe should land on the neutral bar at the main panel. The neutral bar should be bonded or the same as the ground bar in this panel (main panel).
can i ad ground bar to ground new ckts that are added to panel
most panels have provisions for you to do so.
Just to clarify for us slow readers, is the panel in question the "service panel" (first means of disconnect) ?
Yes but that is not you were talking about in your first post.
Can you answer Augies question as to whether this is the service panel?
Roger
And for further clarification in addition to Augie's question, are you saying that you think it is a problem for the grounding electrode conductor to land on the neutral bar at the service panel?