I may not fully understand your situation, but, in general you protect a conductor at it's ampacity.
If you had a breaker of fuse providing 400 amp protection, the 10 ft tap rule would allow you to tap onto the 400 amp feeder with a conductor with an ampacity less than 400 amps if you comply with the tap rules.The 10 rule allows a conductor with 10% of the OCP rating to extend to a overcurrent protective device sized to protect the smaller conductor.
I picture a wireway or j box with 400 amp conductors and one or more 50 amp taps to overcurrent devices.
It is pure conjecture on my part, but I would assume the customer is providing for future load and this would be the 1st of many taps.