chris kennedy
- Miami Fla.
- 60 yr old tool twisting electrician
i clip out about 2" long so it can't touch anything.
300.14.....
Chris look at the exception. That is why I didn't cite the article.300.14.....
I agree with Chris.
No exception for the OP question.
Cutting the wire makes it a code violation.
As to the wirenut. I understand how that could help.
300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points.
At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening.
Exception: Conductors that are not spliced or terminated at the outlet, junction, or switch point shall not be required to comply with 300.14.
I agree with Chris.
What does the exception mean. I must not be thinking straight. I believe I can run a 14/2 without ground if I wanted. Of course if the fixture gets changed then it is a violation.
How do you figure the exception doesn't apply in the OP's case?
The wire terminates in the 'box'.
If that were true, what would be the point of the exception, since everything discussed in 300.14 is in the 'box'?
I'm still not following it. 300.14 is talking about the conductors in a box, etc. The exception is talking about conductors that aren't spliced or terminated inside of the box. That would leave me to believe that the ground wire cut short is code compliant via the exception (altho hack work).
The short or cut wire IS terminating in at outlet. So it does not meet the exception.
If you have the handbook look at exhibit 300.13.
This applies to ALL conductors.
I only have the handbook in 2005 and the Exhibit doesn't match up:
Exhibit 300.13 Raceways used to support Class 2 thermostat cables.
I actually have never had a problem with any I have installed. EVER.
I, however, have been in countless that have shorted out. The wirenut is not a bad idea. Me personally, I clip out about 2" long so it can't touch anything. I was just agreeing with the wirenut idea, even though I don't do it
I don't think the NEC is concerned about wasting time.If you cut the ground at 2" the next guy has to waste time making a pig tail.