Do I pull in a neutral or a ground with my parallel conductors and then what size?
The system is:
1500kVA service from utility owned pole mounted transformers, 12470/7200 primary with 100 amp fuses.
480 center grounded Delta secondary (yeah, I know - all they would give me, I have no 240 volt loads) feeding a 2000amp fully rated breaker in a 3 phase 3 wire MCC.
transformer X0 is grounded
I think I have to have parallel runs of 600kcmil (MCC lug limit) and full 600kcmil neutrals. I think the full size neutrals are required per the "delta" requirment of 250.24.C.1
Is this correct? I have a consultant that is saying I need to pull an equipment ground and don't need the neutral. I still calculate this to be 350kcmil if required based on upstream fuse size.
Which is it? - or is it something else.
The system is: