Per the wording in the NEC, I think so.
Per enforcement I think not, how is this any different than a flush mounted panel board?
Gotta wonder what sins that plywood sofit is hiding. :grin:
FWIW I think the house keeping pad is also a violation that is just
accepted.![]()
I see the housekeeping pad in the picture as a 110.26(A) violation....
I consider house keeping pads a trip hazard if it sticks out to much past the front, I don't care if it's three feet past the front.
With these plywood walls above the MCC. Do you consider this violating 110.26(F) dedicated equipment space?Thanks.
Yes the section does need work. It is my opinion that there is no way to install a flush panel without violating this section based on the current wording.If it does then every flush mounted panel I have ever done would be in violation, I can see this is a section of code that needs some work.![]()
The issue would be 110.26(F)(1)(a).I dont see a problem here. I just pulled out my code book and I dont see anything that would violate it.
And before you say the wall is not equipment, take a look at the exception. It appears the CMP thinks that a suspended ceiling is "equipment" so I would conclude that the wall is too.(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
But if the inside dimensions of the "wall" are exactly the same as the dimensions of the equipment, a violation would not occur. Now does 110.26(F)(1)(a) interpret "space equal to the width and depth" to be the entire equipment itself or simply its 'wiring entrance locations".The issue would be 110.26(F)(1)(a).
And before you say the wall is not equipment, take a look at the exception. It appears the CMP thinks that a suspended ceiling is "equipment" so I would conclude that the wall is too.
Gotta wonder what sins that plywood sofit is hiding. :grin:
FWIW I think the house keeping pad is also a violation that is just accepted.![]()
But if the inside dimensions of the "wall" are exactly the same as the dimensions of the equipment, a violation would not occur. Now does 110.26(F)(1)(a) interpret "space equal to the width and depth" to be the entire equipment itself or simply its 'wiring entrance locations".
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
The issue would be 110.26(F)(1)(a).
And before you say the wall is not equipment, take a look at the exception. It appears the CMP thinks that a suspended ceiling is "equipment" so I would conclude that the wall is too.
I don't think the cmp was thinking a wall is equipment, they were just distinguising what is a structural ceiling. So I'm going with wall is not equipment.