I do a lot of troubleshooting. A LOT. But, I haven't had to deal this specific problem in a while. I was hoping someone would have a better mouse trap as it were.
Situation:
300,000 square foot steel building. Silent Knight IFP-100 (a.k.a Silent knight 5808)
About 110 devices on the SLC, mostly Addressable Input modules, some Mini input Modules and Relay modules.
SLC class B and T tapped at the panel, in other words there are 4 legs of the SLC home run to the FACP.
Almost half of the devices are on the "bad" leg.
All FPL above the bar joist. FPL in EMT down to pull points and devices. Some of the monitored contact wiring are underground outside to monitor a fire suppression water tank. The Addressable input module is IN the building. This is in PVC, with a UG rated FA cable of some sort.(I'm not sure is 100% code compliant, and we'll deal with that later.)
When metering the one side of the leg that I believe is the problem, no ground fault is detected (about 26 Meg Ohm actually, the other three legs are similar in readings not causing a GF, the threshold for GF in the panel is 40K Ohm)
When it is attached to the FACP, the GF condition returns. However, it randomly goes away, so right now its normal.
When this occurs and the GF condition is present on the panel but not on my meter, typically the GF is on the monitored side of a addressable input module (kinda like the load side of a circuit, but not.)
No exact drawings exist.
Since the GF is transient, do I just resign myself to opening every box that has a device in it on the bad SLC leg?
Or would you have a better idea?
Situation:
300,000 square foot steel building. Silent Knight IFP-100 (a.k.a Silent knight 5808)
About 110 devices on the SLC, mostly Addressable Input modules, some Mini input Modules and Relay modules.
SLC class B and T tapped at the panel, in other words there are 4 legs of the SLC home run to the FACP.
Almost half of the devices are on the "bad" leg.
All FPL above the bar joist. FPL in EMT down to pull points and devices. Some of the monitored contact wiring are underground outside to monitor a fire suppression water tank. The Addressable input module is IN the building. This is in PVC, with a UG rated FA cable of some sort.(I'm not sure is 100% code compliant, and we'll deal with that later.)
When metering the one side of the leg that I believe is the problem, no ground fault is detected (about 26 Meg Ohm actually, the other three legs are similar in readings not causing a GF, the threshold for GF in the panel is 40K Ohm)
When it is attached to the FACP, the GF condition returns. However, it randomly goes away, so right now its normal.
When this occurs and the GF condition is present on the panel but not on my meter, typically the GF is on the monitored side of a addressable input module (kinda like the load side of a circuit, but not.)
No exact drawings exist.
Since the GF is transient, do I just resign myself to opening every box that has a device in it on the bad SLC leg?
Or would you have a better idea?