I was told by an electrical inspector that SE/SER cable had to be sized using the 60 degree column of 310.16 unless it is the main service or feeder for a dwelling unit. I can not find any tempature limitation for SE/SER cable except for the terminals that I'm using and the conductors xhhw-2?
Welcome to the forum.
Here ya go:
338.10(B)
(4) Installation Methods for Branch Circuits and
Feeders.
(a) Interior Installations. In addition to the provisions
of this article, Type SE service-entrance cable used for interior
wiring shall comply with the installation requirements
of Part II of Article 334.
334.80 Ampacity. The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The ampacity shall be in accordance with the 60?C (140?F)
conductor temperature rating. The 90?C (194?F) rating
shall be permitted to be used for ampacity derating purposes,
provided the final derated ampacity does not exceed
that for a 60?C (140?F) rated conductor.
Okay, now Gus and Dennis can argue about 310.15(B).:grin: