I have a residential job with a 400A service feeding two 200A main breakers in separate enclosures. Someone did a generator job on this service by installing a 200A Single Throw disconnect and feeding the load side of each breaker. To me it was always a given that double throw would be required. But I can not find it in the code, least not in the service part.
So my question is? where can I find in the code the part that deals with this? Another question is, if I change this to a double throw switch, fed from the meter then use three wire lugs ( I have to add another main disconnect) and feed the three mains from the disconnect does the disconnect has to be fusible? and if not I assume the tap rule applies from the load side of the disconnect to the mains. The meter, mains and disconnect are all grouped.
Thank you.
Thank you.