jango Senior Member Sep 3, 2010 #1 Can I get some input on whether or not it is required to put a 240 volt steam shower unit on a GFCI protected circuit? Thanks.
B bobserrano Member Location Silicon Valley, California Sep 3, 2010 #2 Manufacturers installation instructions should set you in the right direction.
Steviechia2 Senior Member Location Massachusetts Sep 3, 2010 #3 The code does not require it, but I like the idea of putting this on a GFCI circuit.
C curt swartz Senior Member Location San Jose, CA Occupation Electrical Contractor Sep 3, 2010 #4 Most steam generators specifically state do not connect to GFCI circuit breaker.
mcclary's electrical Senior Member Location VA Sep 3, 2010 #5 curt swartz said: Most steam generators specifically state do not connect to GFCI circuit breaker. Click to expand... True, if you wired ten different kinds, I bet 8 of the 10 would not requireGFCI protection
M macmikeman Senior Member Location Planet macmikeman Sep 3, 2010 #6 When they are the kind that heat up wet rocks the instructions are pretty specific to not use a gfi protective device on all the ones I have wired.
J jusme123 Senior Member Location NY Occupation JW Sep 4, 2010 #7 mcclary's electrical said: True, if you wired ten different kinds, I bet 8 of the 10 would not requireGFCI protection Click to expand... is there any specific reason for this?