Locknuts for bonding History

Status
Not open for further replies.

fritts

Member
Does any one know when the bonding of metal raceways was first mentioned in the code, especially the acceptance of the locknuts in 250.96.
Having a dispute on a building unknown age (really old) with metal raceways some installed with locknut on one side metal bushing on the other side.
Thanks in advance for any input.
 

Buck Parrish

Senior Member
Location
NC & IN
Here's a quote from a book called Electrical Contracting author Auerbacher, Copy right 1908
"Boxes used in concealed work in fireproof buildings are fastened to the conduit by means of a locknut and bushing, and wherever a conduit terminates the bushing must be used"

It goes on to mention the "two wires in the conduit". This leads me to belive the conduit was being utilized as a ground. My collection of NEC books only goes to 1947.
 

480sparky

Senior Member
Location
Iowegia
The bulk of the language of 250.96 goes back to the 1971, where it appears in 250-75. Similar language appears as far back as 1953 as Art. 2574
 

R Bob

Senior Member
Location
Chantilly, VA
Anybody ever seen locknuts spot welded to the enclosure?
I've seen this in older bldgs. on service equip.
I suspect that grounding bushings took the place of this method.
Any background on this?
 