that should be complete system ground test?
Yes, like Brian said, "Ground test" is a little vauge. You need to know what you are requesting to be tested. However, any testing company worth squat should have asked you. 80% of real testing companies are pretty good, but there are some out there that "say" they do testing but really just do it as an added service. You want a firm that does nothing else.
You should spec this:
NETA ATS?2003
Section 7.13
Grounding Systems
1. Visual and Mechanical Inspection
1. Verify ground system is in compliance with drawings, specifications, and NFPA 70 National Electrical Code.
2. Inspect physical and mechanical condition.
3. Inspect anchorage.
2. Electrical Tests
1. Perform fall of potential or alternative test in accordance with ANSI/IEEE 81 on the main grounding electrode or system.
2. Perform point-to-point tests to determine the resistance between the main grounding system and all major electrical equipment frames, system neutral, and/or derived neutral points.
3. Test Values
1. The resistance between the main grounding electrode and ground should be no greater than five ohms for large commercial or industrial systems and 1.0 ohm or less for generating or transmission station grounds unless otherwise specified by the owner. (Reference ANSI/IEEE 142)
2. Investigate point-to-point resistance values which exceed 0.5 ohm.