I'll agree with that up to the point where the primary EGC is used in lieu of an available local electrode.However, nothing says you have to run a separate conductor to make this connection to the required GE. If the EGC is a conductor (as opposed to a raceway) and it is of the appropriate size all the way to the GE it has to be bonded to, there is no need to run another conductor. Just use the EGC.
But that'll likely change once under the 2011 NEC cycle, where we will likely not be able to use an EGC as a GEC.