Buck Parrish
- NC & IN
Does anyone know where to get a ground clamp. My ufer ground was cut . number four solid copper. This connection will be buried. I am not typing. I am speaking this message to my phone in the field.
You are correct that the splice has to be listed for bonding and grounding for this application. Some compression butt splices are so listed and some are not.Thanks for the info. I don't know why but i was thinking it had to be listed for the grounding. Sounds like a regular underground splice kit will work
250.64(C)(1) Splicing shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
Are you from the future?
No, this technology has been around for a while.
It's just getting better and easier to utilize. Beats the heck out of finding all those little keys on the phone.
It has keys? :grin::grin:I can't even see those little keys on the phone:grin:
It has keys? :grin:
This has always seemed like a bit of a loop-hole to me and please tell me if I'm wrong, but I think the only place the requirements of 250.64 apply are on that single conductor from the disconnecting means. The connections between the electrodes are covered by 250.68 which is a bit less restrictive. It requires a listed connection, but not a connection listed for grounding.
My point in the OP's case is that I think he's met the requirements if he attaches the cut UFER ground to the rest of the GES with any listed connection and has an unbroken GEC from the main disconnect to any point on the GES.
Mark
Well. That makes it interesting. Is the tail piece of conductor part of the GES or the GEC?? I don't know. I would guess it's part of the GEC. However, I think you could meet the requirement (technically) by adding a ground rod, attaching the UFER tail to the ground rod with a listed connection, and then attach the GEC to the new GES at any point. Sounds stupid, but I think it would meet code.
Mark