- Chapel Hill, NC
- Retired Electrical Contractor
I only want Cuban.I think Dennis wins the prize on this one. Give the man a cigar. :grin:
Correct... 150% of the appliance rating- that is 16.24 *1.5= 24.4. I had a typo in my last part of the other post- I had 15.25 instead of 16.25....Thanks Dennis for the 422.13 guidance. I appreciate the knowlege I gain from this site.
To make sure I understand, the calculated load is 16.25 amps. The branch circuit must be rated at 125 % of this = 20.3 amps. 422.11(E)(3) applies to the 16.25 amp load = 24.4 amps not the 20.3 amps @ 150 % = 30.5 amps. Right?
I would leave it at 30 so if when they replace element with a true 4500/ 208 it is ready. Is no hazard just lower voltage resulting in lower load. Kinda nit picking for nothing
I give jim the the cuban cigar , since the name plate doesnt show 208 , a person could connect to 120 v and not be any worse violation than 208 if it is a violation at all , and yes it will get hot eventually I know because during storm I got some hot water from a 120 v generator by moving one of the hot on breaker to neutral. So every one is saying I should have changed the breaker to 9.37 x 150 = 14.07 or 15 amp ? I will be sure to do that next time till storm passes LOL
I had small trailer many many years ago and put in water heater 20 gal 240 on 120. Was better than ice cold water but not much
back then i was not an lektican or plummermaybe I should not have said hot, it would if covered with insulation enough, the low wattage is not a lot above the heat loss thru the WH, You could have gotten a 120v element to install in the WH you know , will heat the 20 gal just fine
Okay let's assume that the heater is listed for 208 volts-- not sure why it wouldn't be....
As the OP states the wattage, using ohm's law, at 208 volts=3380. Divide by 208 and we get 16.25 amps.
Now go to 422.11(E) -- the ocpd cannot be larger than 150%-- 15.25 equal 24.4 amps. Thus, IMO a 25 amp breaker is req as (E)(3) allows you to go to the next standard size from 24.4-- that is a 25 amp breaker.
422.11(E)(3) requires a maximum of 150% of the rated current. This water heater is rated at 4500 Watts @ 240 volts. I would say that the water heater is rated at 18.75 amps. Just because we apply a lesser voltage doesn't cause it to loose its ability to handle 18.75 amps. 150% of 18.75 amps is 28 amps. Next size up is a 30 amp breaker