Is tape "listed" for this + an overheating question

Status
Not open for further replies.
look to me a MWBC neutral is overloaded
The two left side breaker look like they are the same phase and the 2 on the right the other phase. 12/3 +MWBC + two breaker same phase= neutal overheating!!!
 
overheated nuetrals

overheated nuetrals

i think it's probably red and black wires on same phase.this could happed with fpe wafer breakers if someone didn't know better
 
FPE? The breakers failed to trip on an overload, and the neutrals happened to be torqued worse than the ungrounded conductors, would be my guess.

Edit: I suppose the hots could look about the same, no photo of that.
 
Status