3 or 4 Wires
CIECO
I have a 500? overhead run to a temp trailer. 120/240 volt. Do I use 3 wires and ground rod or 4 wires and a ground rod?
What code cycle are you under? For the 2005, I'm guessing that 3 conductors may be all that's required if 250.32 applies.
That is what I think but I am not sure? (05) Look at 250.32 (1) & (2)
3 or 4 Wires
It would depend if the temporary service in the design and under what Code cycle it was approved. If the temporary service is not in the design it would have comply with the current Code.
I have a 500? overhead run to a temp trailer. 120/240 volt. Do I use 3 wires and ground rod or 4 wires and a ground rod?[/QUOTE
It looks like exhibit 250.17 in the NEC handbook only shows 3 wire for the feeder from panel in one building to panel in another building there is a neutral but no EGC but each panel has a ground rod. That is very confusing because a mobile home fed from a disconnect on a pole requires 4 wire with ground rod at disconnect but not at trailer panel