DP contactors... DP should stand for "Don't Purchase" instead of Definite Purpose.
DP contactors are ONLY to be used in engineered OEM systems where everything about them is specifically tailored to known quantities and qualities that are controlled within the OEM assembly. One big issue is that the coils do NOT have the same kind of voltage tolerance that you find in other contactors like NEMA or IEC. If the coil says 110V, they usually mean 110V, not 120V. If you feed it 120V it fries and vice versa; if the coil says 120V and you feed it 110V it fries. There are no NEMA design spec guidelines that apply to DP contactors, you get what you pay for.
That said, you should also observe the operation BY THE PHOTO CELL, not your over ride test. It could be that the photo cell is "chattering" between on and off in low light conditions and that chatter is going to fry your coil.