480 volt service
Jodonnell
I am working on providing a price for a church renovation. The plans originally called for a 120/208 volt service. The size was 1200 amps and they only had one patch of egress. The electrical inspector caught this in plan review. They have re done the drawings and sent them back out to bid. They have now changed the service to a 277/480 volt service at 800 amps. They are re-feeding the existing electrical via a transformer. They only have 480 volt RTU loads and re feeding the existing which is also 480 volts. So there is no need for a neutral. Is there anything in the code that would allow me to provide an alternate price for a 480 volt service instead of a 277/480 volt service.
If the POCO secondary is a wye, I believe the grounded conductor needs to be connected to your service as per 250.24(C).
In my area I have never seen a POCO supplied 480 volt transformer that was not grounded. All the ungrounded systems I have seen in industrial establishments have primary services with customer owned distribution transformers.