Lightning Protection

Status
Not open for further replies.

ampal

Member
Location
Houston, Texas
If you have a lightning protection system with a ground loop, I know you are required to have a downcomer every 100ft. But my question is since you have the loop, does the downcomer still have to terminate in a ground rod?

Thanks
 
But my question is since you have the loop, does the downcomer still have to terminate in a ground rod?
No there is no requirement to do that. However from a design POV you do not want to connect the down conductors to the ring. You want to drive a rod and connect to the down conductor.

The only place want to bond the two together is at the service entrance.
 
No there is no requirement to do that. However from a design POV you do not want to connect the down conductors to the ring. You want to drive a rod and connect to the down conductor.

The only place want to bond the two together is at the service entrance.

What about exhibit 250.31?
 
I see, thanks guys, it seems that the ground ring and well are connected indirectly, I've seen some designs where the downcomer crosses the ring and terminates in a ground well..
 