Conductor Size for 480 Vac @ 430 Amps ?

Status
Not open for further replies.

dwirebender

New member
I am trying to size the conductors in my measurement enclosure.

I have 3 conductors passing through current transformers to measure the load of tested equipment.

The enclosure is a 36 x 60 x 12. Except for measuring equipment there is noting else in the box.

How do I size this conductor.

Max load is 480 VAC at 430 Amps. It will vary.

350mcm welding cable has been suggested.

Obviously I'm looking for the smallest possible conductor.

DLO is also an option.

Can I get an opinion from someone...?
 
Is the conductor entering the enclosure in conduit? Continuous Load?
One circuit or more?


Size 60C 75C
1/0 125 150
2/0 145 175
3/0 165 200
4/0 195 230
250 215 255
300 240 285
350 260 310
400 280 335
500 320 380
600 355 420
700 385 460
 
Is voltage drop an issue? How long of a run?

262.6 MCM DLO is good for about 460A and is about 1" OD if memory serves.
 
Last edited:
rather than run huge wires like that is there some place you can put the CTs where the wires already are? they don't take up much room.
 
Another reason not to use DLO or Welding cable is that you MUST use approved connectors for it. Most off-the-shelf mechanical lugs and compression lugs are NOT rated for use on those fine strand cables. About the only thing legal to use on them are specifically rated compression lugs and a lot (most?) suppliers don't have them readily available, they have to order them.

Another good article on the subject, albeit for the PV industry, it applies to all uses of those cables.
 
Is voltage drop an issue? How long of a run?

262.6 MCM DLO is good for about 460A and is about 1" OD if memory serves.
I assume that ampacity came from the cable manufacturer. If so it is based on 90?C and in free air. That ampacity cannot be used for NEC applications. Also, you can't even use the DLO for NEC applications unless it is dual listed as one of the cable types found in the NEC.
 
I assume that ampacity came from the cable manufacturer. If so it is based on 90?C and in free air. That ampacity cannot be used for NEC applications. Also, you can't even use the DLO for NEC applications unless it is dual listed as one of the cable types found in the NEC.

Okay, so even though I am an idiot, I am not crazy(maybe).

350 kcmil, or whatever is similar in DLO, is too small?
 
Okay, so even though I am an idiot, I am not crazy(maybe).

350 kcmil, or whatever is similar in DLO, is too small?
Most of the dual listed DLO I have seen is listed as RHH, so I would use the 75?C ampacity of 350kcmil from Table 310.16.
 