W wyboy Senior Member Sep 21, 2010 #1 It is my understanding that the neutral (grounded conductor) on a four wire, 208, three phase feeder (wye) does not count as a current carrying conductor for derating when more than three current carrying conductors in a raceway. Is this correct?
It is my understanding that the neutral (grounded conductor) on a four wire, 208, three phase feeder (wye) does not count as a current carrying conductor for derating when more than three current carrying conductors in a raceway. Is this correct?
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Sep 21, 2010 #3 Correct, but take a quick look at 310.15(B)(4), make sure that doesn't apply to you.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Sep 21, 2010 #4 This is a good article to look at. It discusses this issue and more. http://ecmweb.com/nec/code-basics/electric_conductor_size_matters/
This is a good article to look at. It discusses this issue and more. http://ecmweb.com/nec/code-basics/electric_conductor_size_matters/