Porch light on Photo-cell
Sierrasparky
USA
Electrician ,contractor
Hey I was wondering this: I recently have seen an installation where the porch lights of each townhome was on a sperate photocell so they all come on about the same time. Each is on the indvidual units breakers so no common area power used. There is no wall switch to turn off the light for servicing. The photocells are in a dark area and are on most of the day. The Photocells look like they were put in an non visible area that is dark so that is would not obscure the facad.
What I wonder is it ok for there not to be a switch other than the branch breaker to turn it off for service. This is residential .
Thanks
210.70(A)(2)(b) requires at least one wall switch controlled lighting outlet to be installed on the exterior side of outdoor entrances or exits. A photocell would not be compliant with this section.
Chris
Thanks
This is an acceptable method. Not great but acceptable.
I guess when an owner gets fried changing a broken Lamp the builder might change his methods.
Thanks
Yes - 410.141 08
Exception to (A)(2)(b): In hallways, stairways and at outdoor entrances remote, central, or automatic control of lighting shall be permitted.
Sorry Chris, I'm with you most of the time.
How is 210.70(A)(2)(b) satisfied? This section requires a Wall switch controlled lighting outlet.
Chris
Just looked at that and there is an exception
at outdoor entrances, remote ,central or automatic control of lighting SHALL be permited.
So I guess it's ok to be unsafe here.
My bad, I should have read the exceptions.;):)
Chris
Had an inspector try to tag me once on this. Attached garage was changed to office for the model and the 2 coach lights were swithched from front door. I called him and asked him if he read the exceptions. He was honest about it and did not know about them. He was nice about it and said he was sorry and signed me off. Happy ending