ware house lighting

Status
Not open for further replies.

sleepy

Senior Member
i have a couple of questions i thought maybe you could help?
in a warehouse, when using cord and plug for each fixture, 277volt on a 30amp citcuit:
what is the max distance of the cord and plug, i am thinking 6ftbut could
not find it in the code, and what is the smallest gage sj cord allowed?
any help would be helpful
thanks
 

raider1

Senior Member
Staff member
Location
Logan, Utah
There is no maximum length limit for a cord and plug connected luminaire. 410.62(C) gives you the requirements for cord and plug connecting electric discharge luminaires.

As for the ampacity of the SJ cord check out 400.5.

Chris
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I agree, no limit on the cord length. But Chris's reference tells us that the outlet has to be directly above the luminarie.
 