J johnnyw Member Sep 25, 2010 #1 when calculating a service is a hot tub and or pool considered if so where would i find in code book?
when calculating a service is a hot tub and or pool considered if so where would i find in code book?
LEO2854 Esteemed Member Location Ma Sep 25, 2010 #2 johnnyw said: when calculating a service is a hot tub and or pool considered if so where would i find in code book? Click to expand... Read ARTICLE 220 Page70- 58 and ARTICLE 680 PAGE 70-558 2008 NEC.
johnnyw said: when calculating a service is a hot tub and or pool considered if so where would i find in code book? Click to expand... Read ARTICLE 220 Page70- 58 and ARTICLE 680 PAGE 70-558 2008 NEC.
cadpoint Senior Member Location Durham, NC Occupation Electrician - but not by NC Law. Sep 26, 2010 #3 image of article 680 image of article 680 This is some of what's covered in Article 680
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Sep 26, 2010 #4 johnnyw said: when calculating a service is a hot tub and or pool considered if so where would i find in code book? Click to expand... You will not find anything that specifically states the hot tub load must be considered. This would fall under 220.14- other loads.
johnnyw said: when calculating a service is a hot tub and or pool considered if so where would i find in code book? Click to expand... You will not find anything that specifically states the hot tub load must be considered. This would fall under 220.14- other loads.