Yes you can....
L.R.T.'s? Little Red Thingies?You need to still use the L.R.T.'s when terminating the MC.
Of course, both replies to the OP are correct. The tricky part is properly supporting the MC. The 330.30(D) rules do not apply if the MC is longer than 6' (that is wirenut to wirenut), and if your troffers are separated by a four foot tile, I doubt your MC will be less than 6'.
330.30(D)(2)Is not more than 1.8 m (6 ft) in length from the last
point of cable support to the point of connection to
luminaires or other electrical equipment and the cable
and point of connection are within an accessible ceiling.
For the purpose of this section, Type MC cable
fittings shall be permitted as a means of cable support.
That is fine with MC cable in a drop ceiling and its not hard at all to support if its longer than 6' its not a prob. Use the caddy supports. I call them bat wings I dont know the real name of them but they look like batwings. They attach to the grid wire and hold the MC cable into place. I like also the quick connects the best vrs the ones with the set screws. They come with a insulated throat(red) which most think is suitable as a little red head (anti short bushing) but its not. You need to still use the L.R.T.'s when terminating the MC.