I was at a building that we finished a couple years ago that the following happened.
During a storm around 2:00 AM there was a loud clap of thunder and lightning which appeared to be very near the facility (there does not appear to be any physical lightning damage to the structure). Just after the lightning the 1000A 480/277V 3 Phase main breaker tripped and the generator did not start.
Review of the generator found that multiple circuit boards had been fried. I am waiting on a response from the generator manufacturer on the cause.
There is an internal TVSS unit which shows on its counter that it has not been hit and all of the LED indicator lights are on.
There is not a Lightning protection system on the building.
What are some possible causes to make the 1000A Main breaker trip?
-Ed
-Ed