What size is the OCPD?
Sure esp. since the #10 is good for 27 amps. Did you run #8 for voltage drop and you are concerned about the #10at the end of the run being a problem. It doesn't matter where it is in the run.Max Fuse/Brk is 40A not sure what the min ampacity is. Let's say its 27.8 can you down size your wire like that at the end of a branch circuit ?
It is not an issue. You could label it in the panel if that makes you feel better but anyone that changes the breaker should know better esp. if max OCPD is 40 amps. Also the 50 amp on the #10 probably wouldn't be a problem.The concern was later on someone could see a #8 in the panel thinking they could put a 50A brk on it but the end of the run is only 10awg
Metric, please.![]()
"Noah!"... .055 x .138 x .152 cubits.
Question is can you run a #8 CU branch circuit to a non-fused A/C disconnect and the downsize the conductors in the A/C whip to 10AWG CU ?? I always thought you could not downsize the circuit at the end of the run. Just can't find a code reference saying so.