Given a system with the following multiple feeds:
Normally, I believe, you'd need a 4 pole Transfer Switch to move from PoCo feed to the backup inverters. But suppose all share the same single point of neutral bond to ground, the building's Ufer+whatever rods? Is neutral switching still required?
1] The inverters have "line" and "load" connections. If/when there's a generator feeding the line side, they kindly sync up to its output and assist, or consume gen. power to recharge their battery plant.
- 277/480Y from PoCo xfmr
- same from 3ph inverters
- pad mounted gen feeding inverter line side [1]
Normally, I believe, you'd need a 4 pole Transfer Switch to move from PoCo feed to the backup inverters. But suppose all share the same single point of neutral bond to ground, the building's Ufer+whatever rods? Is neutral switching still required?
1] The inverters have "line" and "load" connections. If/when there's a generator feeding the line side, they kindly sync up to its output and assist, or consume gen. power to recharge their battery plant.