G gbuschling Member Location Chesapeake Beach, Md Oct 5, 2010 #1 I am running 4-4 MC cable to feed a sub panel. Is an insulated bushing required in the panel? The bushing hardly even bites on the connector.
I am running 4-4 MC cable to feed a sub panel. Is an insulated bushing required in the panel? The bushing hardly even bites on the connector.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Oct 5, 2010 #2 MC and MC connectors do not require bushings.
raider1 Senior Member Staff member Location Logan, Utah Oct 5, 2010 #3 I agree with Larry, 300.4(G) does not apply to cables just to raceways. Chris