Voltage Drop
Benton
Louisiana
In the section of the code book under the Tables, Conductor Properties, which of the resistance percentages do I use when calculating voltage drop? I have been taking a quiz and my answers seem off.:-?
Single Phase VD= Amps*Length*ohms*2?
3Ph VD=Amps*2L*R ?
Thank for your help in advance
3Ph VD=Amps*2L*R ?
Are you using table 8 or 9. IF it's Ac current you should be using reactance (table 9) not DC resistance (table 8).
Resistance Value used for 3-phase voltage drop
From the voltage drop formula (Mike Holt WireGuide99), the "Equiv CCT AC Resistance" value used in the 3-Phase voltage drop calculation is (1.732) x the AC resistance value from NEC Chapter 9 Table 9.
The "Effective Impedance" (Z) is also listed in table 9 for Ohms to N (1000 ft).
Why would the effective impedance not be used for this calculation?