hurk27
- Portage, Indiana NEC: 2008
Ok I have a small job to put controls to a mixer.
Let me start with what the application is.
The mixer is an ex large cement truck back unloader, mounted on a frame bolted to the floor in a place that processes material for the mills, it has a 20 HP standard 9 lead motor with E class insulation, 1750 rpm's belt driven through what looks about a 4:1 ratio to a gear drive unit that has a 11:.89 ratio the gear drive has about a 6" sprocket that drives a chain around a 5' sprocket welded on the back of the mixer drum.
Motors voltage is 230/460
FLA is 57/28
plant power is 208/120 3/phase 800 amp MDP
Now I was told this setup was originally controlled by a 3-pole transfer switch (nothing surprises me:roll
that would reverse two leads in one position from the other and a NEMA 3 starter.
The new owners would like to have speed control and reversing jog capability.
I have already told them that to use this motor under the rated speed we would have to add additional cooling fan independent of the motor speed, to the back of the motor, and I could not guarantee the life of this motor, they said that they didn't care as long as it got into operation and they will purchase the proper inverter rated motor at the time this one fails.
For the most part the motor will run full speed in FWD, but since in reverse is has to be controlled to empty the drum, inside the drum are flights that form a screw to back out the material.
Now the question?
I have been pouring over the details on so many VFD's I seem over whelmed.
Can any one narrow down out of the hundreds of VFD manufactures which drive can possibility do the above job with the least amount of programing, and install.
External FWD, STP, REV, And maybe a analog VR for speed control would also work, but would like to keep it simple (cost wise) to the unit to have the required functions on the unit.
Guess it's like HELP
At least who knows of any suppliers who would have a tech line to discuss which drive to use, I was trying to deal with the Drives Warehouse but ran into a dead end with them.
FLA is 57/28
Now the question?